AB VFD PowerFlex 525 speed output
LostInIKEA
May 2020
Utah
Hey PLC.net, I'm working with a PowerFlex 525. It's communicating within the panel via ethernet but I need to send the speed out 4-20mA via the analog output. I went into CCW and changed parameter 88 "Analog Out Sel" to "OutFreq 4-20" but when I meter the 14 and 16 (common and analog out), I get 0mA when the VFD is running.
Then I saw that there was a jumper J10 and it was at 0-10V so I changed it to the 0/4-20A one but still nothing
Any gurus out there that can help?
References I've used
http://www.marketotomasyon.com/UserFiles/File/Allen_Bradley/Drivers/PF523_525/520_qs001_en_e.pdf
pg14
https://rockwellautomation.custhelp.../~/powerflex-525-4-20ma-analog-out-sel-set-up
Did you double check on the drive itself that the parameter was set correctly? Did you checked parameter t89 to make sure it is set correctly. I've done it on a project and it was as simple as the manual said. Last thing would be to monitor parameter b001 to make sure that there should be an output.
I have to ask this - what did you use as a load for the 4-20mA signal? as in, did you connect your meter in series?
Have you checked your meter in another 4-20mA circuit somewhere?
Sorry, you probably did this, but I thought that I should verify this.
Ian
Less concerned about the specifics of the powerflex, more curious if a circuit had a disconnect on a motor that was separate of the VFD, is there...
1,805
Greetings all! I am considering the use of a PowerFlex 525 VFD for a 3-phase 1 HP fan motor for an equipment skid that will be shipped to France...
2,262
Hi, I have a potentiometer connected to a siemens micromaster 440 to control a servo motor speed and they are not connected to any PLC. Now, I am...
4,048
This is a new one to me. We thought we were having sensor issues when trying to commission a new machine, but realized that the inputs were not...
2,497
I am getting a motor stalled fault on a VFD for a incline conveyor motor with a electric brake. I notice that when the VFD is supposed to ramp...
4,264