ABB ACH550 halt/limit PID via DI
g.mccormick
Jul 2012
IN
961
Not a PLC question but still controls. I have an application with an ABB ACH550 that I will be adding a sensor to the drive and have the drive use PID to control motor speed using the feedback sensor. What I want to be able to do is to program one of the DIs so that when the DI triggers, the PID loop either freezes, or limits.
The actual application is controlling the room pressure to a slight vacuum with an exhaust fan. When a door opens, I don't want the fan to run away to full speed since this can cause the door to slam closed and I don't need anyone getting their hand smashed. So door switches will be used to hopefully trigger the VFD to either freeze the output or limit the output speed.
Anyone have thoughts?
The manual for that lists some built in macros, including a couple that have dual setpoints, with the setpoint determined by a DI. I am not sure if those a speed setpoints or process setpoints to match a value from a transducer
Thanks I will look into that. Another option maybe to just have the DI set to preset speed and make that preset speed slow. Or I may just use the doors to interuppt the permissive so that the drive can't run without the doors closed.....
I am trying to find information on talking modbus to ABB ACH550 drives with integrated Eclipse bypass controls. I have two air handlers that each...
1,902
I have a customer with an ABB HVAC drive. It is a 3 section drive. Lower section is integral disconnect switch, middle section has bypass...
1,608
Can anyone send me some information about using the msg command to communicate with my ACH 550 ABB Drive? I dont know how to use this command. I...
24
7,610
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
89
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
143