Hi everyone,
i know its not the right place for that sort of question , but i need help so please excuse me .
i have an ABB acs 800 vfd and i am experiencing two problems may be connected together or may be not.
first , my vfd shuts down the controlled motor when the electricity shuts down momentarialy (N.B i have another 3 vfds, this problem isnt happening).
When i turn off the vfd or electricity cuts off and gets back another fault appears.
the code is 5410 int config.
i read the manual , its talking about cleaning optical fibres or something like this.
i need help if someone experienced something like this or may have a solution for it .
Strange. I thought a VFD was supposed to shut down on a loss of electricity.
I remember a very old VFD . . probably first generation . . it was running a conveyor and the installer had it turned on or off with a selector switch. When we had a momentary power loss the VFD would shut down (loss of power) and when the power came back on the VFD would slam power back to the motors - which were out of phase with the VFD and it would blow five or six transistors out of it. We added a control relay which would drop out and keep the VFD shut down till somebody pushed a reset / start button.
Poet.
Poet.
Most modern VFDs now have what's generically referred to a "flying restart" wherein the VFD senses the back EMF of a spinning motor and matches it's output frequency to "catch" it spinning and regain control, avoiding that exciting transistor fireworks display. But yeah, before that came about it was a real problem.
hse112,
As I told you in another forum, this is indicative of a communications problem with the boards and sub-systems within the VFD and is either a bad fiber optic connection (hopefully) or a defective board or output transistor. The fact that your VFD shuts down on a power loss is relatively normal behavior. You said you had other VFDs that don't do this, THAT would be unusual. they likely have something added to them to prevent that.
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
141
Hello Experts, I recently stumbled with an issue about ABB VFD ACS800 connected with B&R PLC X20CP1484-1. This ABB VFD ACS800 somehow got...
323
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,607
Hello all. Working on a centrifuge for a customer. They have ACS880 ABB Vfd's installed, and need them to talk VIA the FENA card Ethernet to...
1,351
I am using a 4-20mA signal from an RTD to an ABB ACH 550 drive. I want to know if anyone has ever set up a PID loop on one of these units before...
1,116