ABB VFD Breaker?

When we design a drive only pannel with 2-3 drive, we like to use a common fused disconnect with fast acting fuse and a manual motor starter for overloading current on each VFD. This device cannot be used alone without fuses. The pannel faulting current is done by the fuses and motor overload,jammed etc is done with the manual starter.

Yes if the VFD short you will get the main fuse blown but in this case, you have a big issue where the night shift guy probably won't be able to solve anyway as the chance to have a programmed spare drive is relatively not likely...
Ok in this case if you had independant fast fuses on each drive you probably could keep the other VFD running but.... it won't make anyone hurt and sometimes quotes are won with few dollars so Specs should have been made clear enought to specify the fonctionnality they want.
 

Similar Topics

Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
156
Hello Experts, I recently stumbled with an issue about ABB VFD ACS800 connected with B&R PLC X20CP1484-1. This ABB VFD ACS800 somehow got...
Replies
0
Views
330
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,619
Hello all. Working on a centrifuge for a customer. They have ACS880 ABB Vfd's installed, and need them to talk VIA the FENA card Ethernet to...
Replies
1
Views
1,354
I am using a 4-20mA signal from an RTD to an ABB ACH 550 drive. I want to know if anyone has ever set up a PID loop on one of these units before...
Replies
0
Views
1,123
Back
Top Bottom