Hi,
I have an issue with COMS with one of my tags. I can't get online to the PLC if I have this one family of tags present. Without it, I can. I'm using CitectSCADA 7.2 SP4 and a ControlLogix L61 PLC on RSLogix v20.04.
Tag in AOI Parameter: CV01_E300.Available
Tag in CitectSCADA: CV01_E300_Available
Address in CitectSCADA: CV01_E300.Available
The errors I get on ABCLX log are (in order):
- Mismatched Message [EIP] (x4, x3 or x2)
- SendUnitData response with CIP error causes session failure [EIP]
- Time Out. Channel Not Initialized [DCB]
- Session Failed [DCB]
I have tried things ie.
1. Sorting variables DBF by IODevice and Data Type
2. Packing, resetting OID
3. ABCLX troubleshooting: http://proscada.ru/ctkbase.en/articles/q4009.html
4. Creating a new variable DBF
Any ideas as to what it may be?
Any help would be most appreciated.
I have an issue with COMS with one of my tags. I can't get online to the PLC if I have this one family of tags present. Without it, I can. I'm using CitectSCADA 7.2 SP4 and a ControlLogix L61 PLC on RSLogix v20.04.
Tag in AOI Parameter: CV01_E300.Available
Tag in CitectSCADA: CV01_E300_Available
Address in CitectSCADA: CV01_E300.Available
The errors I get on ABCLX log are (in order):
- Mismatched Message [EIP] (x4, x3 or x2)
- SendUnitData response with CIP error causes session failure [EIP]
- Time Out. Channel Not Initialized [DCB]
- Session Failed [DCB]
I have tried things ie.
1. Sorting variables DBF by IODevice and Data Type
2. Packing, resetting OID
3. ABCLX troubleshooting: http://proscada.ru/ctkbase.en/articles/q4009.html
4. Creating a new variable DBF
Any ideas as to what it may be?
Any help would be most appreciated.