Does a solid-state module exist that senses 120AC input and triggers a 24VDC PLC input?

And yes, I know I can use a simple relay, but I have multiple circuits to monitor and when I add up the wattage of running all the coils 24/7, it's a surprising amount of W/h each year.

Everything Google is finding goes "the other way" and uses a low voltage control signal to switch an AC load.


Thanks,

rpoet
 
Since it is a lot of circuits, I would suggest using AC input modules for your PLC.


I said PLC to keep it simple. It's actually a device that doesn't have an option for 120VAC inputs. If it were a PLC, that's exactly what I would've suggested.




-rpoet
 
Last edited:
This is exactly what I'm looking for. I dug through Phoenix's website and never saw these. I like PC's products, but their website is terrible! Thanks!

EDIT: Holy smokes! $73 each, and a month+ leadtime. Gotta love Phoenix Contact.


-rpoet


Well, now that you have a part number, ask around for equivalents from your local electronics dealers.
 

Similar Topics

I have a requirement to sense the true power used by a submersible pump so that I can monitor pump performance. Anyone using anything that can do...
Replies
10
Views
2,950
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
Replies
0
Views
39
Hello all, I am currently trying to program a PowerFlex 525, version 7.0. We had a power outage recently and when the power was restored, the...
Replies
10
Views
300
Looking at installing point io, with a 1734-AENTR communications adapter and ten 1734-IT2L modules. In IAB it installs a 1734-EP24DC after every...
Replies
1
Views
77
First time I've used either the software or this unit. This is the setup I have right now. I have 20mA coming into AnalogIP1. Both the Main.PV...
Replies
0
Views
51
Back
Top Bottom