accesing single bit in distributed I/O
Pandiani
Apr 2005
Tz
718
Hello, I've just finished 11th chapter of working with Step7: "Configuring the distributed
I/O, there is example how to configure distributed I/O via PROFIBUS. Example is shown in
attachment. As you can see the module has input addresses 4...5. My question is how to
access a single bit in byte 4 of B-16DI. B-16DI is at address 1 and how to use this info
to access a sigle bit?
I assume that solution has something to do with PI (Peripheral Input) but I'm not sure.
Also, what address 1023* in slot 2.1 DP-Master means?
Thanks for help.
This is a diagnostic address and should not concern you on this issue.
So, it's just that simple? I thought it's something more complicated since analog inputs are treated with PIW.
Anyway, thank you
Yes, analogue inputs are addressed using PIW and PQW, but what you have asked about is a digital input.
The AI2X12bit that you have in slot 6 of the main rack will be addressed using PIW, if you let the system decide the address this will probably be PIW368 and PIW370
Paul
Hello all, I'm trying to access the bits in an array that is defined in a CompactLogix PLC. I imported the L5K to my Crimson project and I was...
2,642
Here is the set up Two PLC5's in Controlnet Hot Backup Two Panelviews sitting on Controlnet Multiple Flexio ACN modules sitting on the Controlnet...
4,381
I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
234
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
105
I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit. The problem is that the analog input cards...
157