i'm comparing the accuracy of some analog inputs
S5 95U 0-10V 10Bit
S7 314C-2DP 4..20mA 12Bit
Endress+hauser SWA70 4..20ma measuring error is 0,125% of span https://portal.endress.com/wa001/dla/5000373/0002/000/03/TI00026SEN_1310.pdf
Working with a pressure sensor and a volume of +- 40000dm³
I know i need to work with the product density
What can be the deviation
10bit = 0 - 1023 = 1024
40000/1024 = 39,0625
12Bit = 0 - 4095 = 4096
40000/4096 = 9,7656
= 40000*0,125% = 50
Am i right ?
Am i right ?
No.
Like many before you, you are confusing accuracy with resolution. The number of bits the A/D conversion uses defines the resolution of the input. In other words it tells you how much the input signal must change before the data in the PLC register changes. For a ten bit input the resolution is +/- 1 part out of 1024, or +/- 0.1%.
On top of that you have accuracy - the variation of the signal or data from the true process value. It includes nonlinearity and zero offset and hysteresis and such. You will never get better than +/- 0.125% because that is the accuracy of the transmitter. Then you have the accuracy of the input card itself, errors from off spec resistors and bad calibration etc. That is often expressed in percentage on the card specs.
So, let's say you have a ten bit card with an accuracy or +/- 0.2%. You total accuracy would be:
Transmitter x Card Resolution x Conversion Error = 0.99875 x 0.999 x 0.998
= 0.9957 or +/- 0.43%
Therefore your maximum error would be +/-172 dm3
If you kept the same transmitter and had a 12 bit input with +/- 0.2% accuracy your maximum error would be +/- 140 dm3.
Hi, I'm using an Allen Bradley 1769-IF4 Analog input crd with a Compact Logix L33ER. Its 14 bit (0-16384), and I'm taking raw readings. I am...
4,595
Hello guys; I'm ashamed to admit it but I can't wrap my head around the proper math to tell a customer what type of accuracy I can get between...
2,845
Hey Friends I am using EZTouch PLC. I am trying to connect with a diameter gauge of 1 micron accuracy through an analog input module. The output...
2,459
I am working on an installation that will require sensor cabling interconnecting sensors to PLC subject to outdoor temperatures. Will the ambient...
2,071
So I have a plc program where most of the outputs are based on a counter that goes from 0 to 1000. The counter speed is adjustable and is...
23
5,962