I am working on an installation that will require sensor cabling interconnecting sensors to PLC subject to outdoor temperatures. Will the ambient outdoor temperatures (-10° thru 100°) affect RTD sensor accuracy? The distance of outdoor temperatures are 90’.
3 and 4 wire RTD sensors compensate for resistance along the cable length. If you are super concerned, install an RTD->4-20mA transducer near the RTD, and run the 4-20 back over the 90 feet.
No, no effect on accuracy as long as
- the RTD is a 3-wire RTD,
- the input is a 3-wire RTD input and
- the conductor size for each of the 3 wires in the cable between the RTD and the input are the gauge/diameter
I worked for a sensor manufacture for several years and "danw" nailed the answer.
With RTD's if you have a 3-wire installation with good connections and same guage wire you will be fine. Just make sure you set the PLC card for three-wire compensation. You can run three wire but unless the PLC / Temp controller are using them it will not do any good.
If there is a lot of electrical interference you could use a three wire cable with a shield and drain and ground it in the PLC panel but this is rarely needed.
Thermocouple on the other hand have a lot of seemingly picky rules that must be followed.
A bit off topic, but I have an old heat trace controller where they used the power cable to get the rtd reading. They have lil pc board at the rtd...
2,013
Hello to all, my name is nagaraj from Bangalore, Actuall i have a RTD PT100 2 wire type and it is fixed 30 meter away from the PLC panel,So...
3,146
I am looking for RTD extension cable that has the stainless steel spiral wrap around it just like public telephones do. Can anyone point me in...
2,947
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,203
Good Afternoon , It seems like we always have problems with using Type J Thermocouples with our slip rings . Would using a RTD at 10...
1,647