Slip Rings for Thermocouples - Is using a RTD ( 10 vdc )better than using a Type J TC
Aug 2016
Virginia
343
Good Afternoon ,
It seems like we always have problems with using Type J Thermocouples with our slip rings .
Would using a RTD at 10 volts , be better than using a Type J that would be generating. millivolts ?
Thanks so much in advance .
+1 For Converting to 4-20 first. Also if you have a lot of IO, I've done ethernet through a slip ring with remote IO.
As Gomez says, Remote IO would be the best, even something like an IO-Link system.
Steve's 4-20 converter on the rotating side would be my #2 choice, but yes, a three wire RTD would still perform better than a TC if going through slip rings.
A big problem with TC's isn't even the signal level, it is that every time you have a new transition connection, with different materials, you are creating additional thermocouple junctions, at different temperatures, and different contributions to the signal.
I've had great luck with wireless battery powered. If i sample in minutes its a few years for battery changes. Faster sampling faster battery depletion.
We did a few non contact IR with 0.25% accuracy if my memory isn't failing.
What's the problem with the Type J's?
durability?
loss of contact with the slipring causes open circuit?
jacket wear?
junction breaks?
noise pickup from grounded element?
Tough to consider a problem is the problem isn't stated . . .
Good Morning , We have a new packaging machine that have Slip Rings . We are using the Slip Rings for a rotary jaw assembly that has heaters...
5,081
One of our factories needs to start an old slip ring motor. I suggested that they use a common "resistor selector" system to start the motor then...
1,896
i don't know much about ac motor slip ring. i have small ac motor slip ring about 2 or 3 hp its possible to me to use VFD, any idea or wiring...
2,346
Anyone ever worked with ABB ASTAT or ABB MoCon drives? Thanks!
1,474
Hi, I have used Vfds for Squirrel cage induction motors. I am now required to use a Vfd with a Slip ring motor. My question is, what do I do to...
2,957