active and passive I/O tags and exact number of signals in DCS
Charbel
Jan 2012
Beirut
307
Dear,
I got first query from client:
Prepare a comprehensive I/O list illustrating signal ( Tag Name, description, type , passive or active , power supply )
What does it mean to have passive and active I/O's included part of the I/O list?
another query from client:
Any calculation signals have to be considered within DCS to get the exact number of compactor’s signals"
I believe calculation signals will be involved only in programming / graphics in DCS but why do we need to exact number of compactor signals?
Thanks for your help!
Best Regards,
Charbel
Assuming we're discussing Fanuc's Dual Check Safety, DCS can be used in place of h/w signals for e-stop and fencing provided the robot is optioned with Profinet Safety or similar.
In the 4-20mA world, passive is a 2 wire, loop powered signal where the power for the signal is connected in the loop, not to the device itself.
'Active' is an analog output powered by a power supply connected to the device, a 3 wire or 4 wire device.
Sizing a DC power supply requires knowing how many loads it can handle.
Active outputs tend to have more issues with ground loops, because of ground potential differences between the receiver (DCS) and the field device.
Can you wire a 1756IF8 analog input card for passive and active instruments at the same time or do they have to be separated. Such as wire 1 card...
4,998
Need a sanity check here. It is possible to have redundant Modbus RTU master, but only one master is actively polling at a time? The background...
2,572
Hi everyone, I have a new (for me) situation with a new job I am working on. I am using the output channel of a 1769-IF4FXOF2F card to send a...
2,644
I need to go from a powered 4-20mA output (i.e. transmitter supplies voltage) to an Allen Bradley HART input card 1756-IF16H. I cannot set input...
2,463
HI, Can tell me the defination of these terms -Master/SLave and Active/Passive in automation field? I found: in computer networking...
4,383