See the screenshot of EIP tag list. We are trying to read in a digital input that is hard-wired. It is shown here as I31.1. I believe we cannot read in specific bits of a tag. What would the nomenclature be for reading in a channel from a remote IO "RS2_AENTR" I know Local IO would be something like "Local:1:I.Ch01.Data"
Some other options
RS2_AENTR:1:I.Data
For the bit address:
Local:1:I.Data[bit_number]
I am unsure of how exactly to address remote I/Os or syntax
I31.1
The goal is to try and display this bit
Some other options
RS2_AENTR:1:I.Data
For the bit address:
Local:1:I.Data[bit_number]
I am unsure of how exactly to address remote I/Os or syntax
I31.1
The goal is to try and display this bit