Thankx and these modules have no problem with being pushed next to each other without any gaps being that the heat vent or on the top,right?
Right. The ventilation is vertical through all the Micrologix as far as I know. We have violated the rules in many cases with the spacing, but as long as the panel temperature is not way over spec., they will run for a long time trouble free until the plastic parts bake...The Micros are more likely to fault and need to be downloaded (or fitted with memory modules) due to brownouts or power cycles and lightning as compared to the SLC or PLC-5. All of our ML1200, and 1500 have been fitted with them to make them automatically recover from these uncontrollable events.
The book will tell you minimum spacing, but that is going to vary depending on the temperature most of all. They are pretty tough little machines. Good grounding is a great start.
You should be fine in my experience, but I don't know the size of the panel and the total wattage of its loads, nor the environment its going in. The spacing requirements are more aimed at avoiding high frequency or high voltage noise. so don't run VFD motor leads right up against the PLC if you can help it!
2. This old system is an OLD PLC-2. All the outputs are going to 120VAC pneumatic valves. With the new Micrologix PLC which is Relay Outputs,I shouldnt have to worry about shunting the outputs right?
For your relay outputs, if the circuits they're driving are solenoids it is never a bad idea to use AC snubbers or diodes for DC to handle inrush/collapsing field currents to extend contact life. I have seen 120vac solenoid valves with power ratings anywhere from 1.3 to 15 watts.
Depending on the coils, you may not need anything. Many of them have suppression or such lower power requirements that you can get 500,000 relay cycles driving them directly.
Interposing relays are highly recommended with a brick where replacing one burnt relay means replacing the controller. Interposing relays means you use nice small "easy to operate" relays (low coil power requirements) and wire them up to the PLC outputs. Those relays then have perhaps as high as 20 amp contacts to drive the "real" load. They can be plug in style relays with din rail mounted bases to make for quick and simple and cheap replacement at the end of their very finite life.
If the output is wired locally to safe loads (under 50% of the max permitted), skip the relays, but, do "know thy loads."
Paul
EDIT: another thread:
http://www.plctalk.net/qanda/showthread.php?t=61045&highlight=interposing+relays&page=2
AND: later on you can correct the original specification and switch to higher density transistor outputs for nearly infinite life of the PLC module by the use of the interposing relay as a sacrificial component doing the hard work.