Using symbol instance addressing doesn't work with Micrologix 1769-L32E

Join Date
Sep 2017
Location
Michigan
Posts
3
Using Rslogix 5000 Data Access manual as a reference

I keep getting 'Service Not Supported' response when using symbol instance addressing to read a tag (Instance ID). Symbolic addressing works fine (Tag Name).

This is for a compactlogix 1769-l32e

Any idea why that would be?
 
Welcome to the PLCTalk forum community !

What firmware are you running on the 1769-L32E ? Those are a second-generation CompactLogix and support up to v20.x firmware.

I found a note in the Knowledgebase (QA27891) that support for symbol instance addressing using function 0x4C started in v21 firmware. I found a mention of that also on page 16 of the Logix 5000 Data Acess Programming Manual 1756-PM020 that you're using.

If your software system needs to support older Logix 5000 family controllers, you'll have to use ordinary tag names or check for the version before using symbol instance IDs.
 

Similar Topics

I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
64
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
124
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
222
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
60
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
111
Back
Top Bottom