Adressing
timodc
Nov 2006
near Rotterdam
Just started working with the Siemens PLC 115U - CPU942B.
I have:
0: 16x 115/230V AC 1A (465-7LA 11)
1,2: 32x DC 24V 0,5A (441-7LA 12)
3: Analoge input: 16/8 channels (465-7LA 13)
This is a better view of the whole PLC/control:
http://stud.hro.nl/0762476/rek.JPG
My question:
I can't figur out, how I can let the PLC proces the Input (of a couple of Volts on the Analog Input) to an Output (of 0/1 on one of the Digital Outputs)? I know you have fixed addresses for the Analog Input (in this case: Slot 3 = 224-255), but how do I use them? Does anyone have a good example?
friendly greetings,
Timo
Hello timodc.
To get an analog input into the PLC, you can use the system function block FB250. You have to specify slot, channel number, the upper and lower limits of the scaled value, and where to store the scaled value.
edit:
You can also access the unscaled value via the in/out image (EWxxx). But you probably better scale the input to engineering values as the first thing.
To control a digital output from an analog input can be done in may ways.
One could be to test for below or above a limit value.
rthiyagu_00 said:
what is the DO you are requiring for yr systeam. Is it limit value monitoring or some thing else? Pl. eloborate
It's more for practicing.. I'm now in my third year of the Higher Education Engineer here in the Netherlands.. that's the third of the four years... and I never got any information on PLC's.. or lessons.. or what so ever.. and now I'm trying to educate myself in the world of the PLC's.. :) so I don't really have specs of "my" machine.. it's just trying stuff out :)
in anyway.. thanks for all the information.. if anyone has anything else that can get me on my way.. please :)
greetings TiMo
I am trying to connect to a Chiller through Modbus TCP that has been setup as a Modbus slave and I see the Rockwell AOI and it looks pretty...
410
Hello Mates, first time developing with deviceNet, Im more used with S7 CPUs. My system is a L23E CPU + PanelView 550 on devicenet. I can't...
788
Hi everybody. I got some problems about how to perform this task Now, I got an FB where I have this code snippet that looks like: L P##DBD_134...
1,147
Hello I got a request to make an exchange table using numeric addressing for a controllogix plc to talk with customer DCS (Delta V) I usually made...
2,399
Gents, I've not had much dealings with indirect addressing, but I'm troubleshooting a program now, and I just wanted to verify that I've come to...
3,013