Alleb Bradley Kinetix 6000 Module Replacement
ghulamshoaib
Feb 2015
pak
Dear All,
can anyone confirm me that if I replace 2094-BM01-S module of kinetix 6000 then would it need to reprogram the device or it will be just plug and play?
Hi
Yes it can but you may need to look at the firmware.
It depends on if your drive is set to display keying
Exact keying and the version your original drive was versus your new drive.
There is NO programming required as all the parameters are stored in the Plc
Hope this helps
Donnchadh
Thanks for reply.
My new Drive showing error E19, while old drive 2094-BM01-S working fine on same motor. can you please tell me what may be the reason?
Hi
That is a position error
Why did you change the drive in the first place ?
What is teh firware version of your Plc and teh firmware of your new drive ?
These need to match as per the tabel on the ab website
As often funny things happen if they don’t
Donnchadh
You should be able to just replace it and go in theory. I had to replace a BM01 over the weekend but all we had in stock was a BM02. Just had to delete the old device, add in the BM02 in its place and match up the axis settings and tag names. Make sure the correct motor gets selected in the configuration and it should take off running no problem.
Hello, i am attempting to set up a new AB IO Link Master. Cat No 1732-8IOLM12R with a CLX L74 v32 though a EN2TR. I set the IP via Boot/P...
607
HI everyone i was trying to upload a program from AB 1769 L32E... But it has given my a firmware version issue.. i am using rslogix v19,so i hve...
4,462
Any one give solution for this fault. We are using AB Gaurd logix controller(5573s), resent days we are facing major fault in controller...
76
Hi how's it going. Was just wondering if someone could help me out. Recently one of the guys over on the LinuxCNC forums put me onto getting an...
346
Hello, Does anyone have one of these cables and willing to open the case so I can see the cable connections inside? 2707-NC5 I have sourced the...
105