I have a problem with a AB 1769 hsc/b module. I want to save a pulse value and I put it into the preset register which will get transferred to the current count register. It works when the module first powers up.

However when I try to do this a second or subsequent time after the module is first powered up it doesn't work. The reset counter function doesn't work as well.

Any ideas???
 
Because the Preset is a Configuration parameter you will have to send a 'Module Reconfig' message to the module. I have attached images showing this code (we are changing the Max Count - a similar type parameter).

When we begin we Unlatch 'Done Counter Reconfig' and Latch 'Doing Counter Reconfig'. This disables counting during this process.

Reconfig.jpg ReconfigMsg.jpg
 
Last edited:

Similar Topics

I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
Replies
14
Views
264
Hi, i want the above to control a 4-20mA valve using the 20mA signal to open the valve fully and a lower signal to partially open the valve how do...
Replies
14
Views
2,565
Hi Guys, Question - does the subject title AB processor act as a processor AND comms module? It does have communications ports available on the...
Replies
2
Views
970
Hello everyone, I am in the beta phase of building a SCADA system. Currently planning to use Inductive Automation as our SCADA platform, but...
Replies
6
Views
2,144
hi, this is my first post in this forum, i have two allen bradley 1769-L30ER and unfortunately I want to make it redundancy. but I heard that...
Replies
12
Views
3,036
Back
Top Bottom