I have an application where I'm using an Allen Bradley CompactLogix plc that has to read registers in multiple GE Fanuc 90-30 plcs. The GE plcs talk to each other via a 'Genius' bus and communicate through an Ethernet hub to an HMI display. Any suggestions on what I need to do/get to enable communication between the AB plc and the GE plcs? NOTE: the cpu in the GE plcs is a 364
Jerry,
You will most probably have to install a communcation card in the CompactLogix and the GE that has a common Protocol. My suggestion would be DeviceNet as I know both of these PLC's support this protocol via additional cards. As far as the GE's go, you would be better off mapping the data from the individual GE's to one GE (via genius) and installing the DeviceNet card on this rack.
Hope this helps you.
Regards,
Andrew Butcher
Jerry,
Genius is a GE Fanuc proprietary network. To the best of my knowledge there is no CompactLogix interface to it.
What HMI are they using? Is there any way it could be used as a bridge between the 90-30s and the CompactLogix?
If you have room to add another module to one of the 90-30s, in addition to the DeviceNet option, there is an ethernet module that will support Modbus/TCP if the ControlLogix supports that. There is also a serial communications module that can be configured for Modbus RTU.
I was wanting to see if anyone had any information on setting up a cub5 meter and getting the data to a Allen bradley PLC. I think i have the set...
139
We have an AB PLC that has a faulty expansion cable between Bank 1 and Bank 2. Part # 1769-CRR3. I found a small burn mark on the board. Being...
766
Hello everyone I have an Allen Bradley Compact Logix 1769-L18ER-BB1B. I have several processes that I would like to start based on time of day...
2,689
I have two L35e processors i want to send message to and from. I just want to do data read. Condition from one plc and see it on another plc. I...
2,226
Above mentioned HMI is installed in my plant with Micrologix PLC. Yesterday the HMI suddenly stopped working during plant operation and HMI's...
4,941