Good morning,
I am onsite at a customer. They have a panel view plus 1500 that does not light up. The screen is always black.
I am not very familiar with these screens, but if I have 120v to the control power terminals is there any reason the screen shouldn’t light up when we touch it? It is entirely unresponsive.
They say in the past. For no explained reason, the screen would just black out in the middle of operations. If they tapped the screen a bunch of times, it would lighten up again.
Note: there is something weird with their control power. I have 120v between line and neutral. But I have only about 60v from line to ground. There is about 60v potential between neutral and ground. This does not seem right, but would it cause this hmi problem?
I am onsite at a customer. They have a panel view plus 1500 that does not light up. The screen is always black.
I am not very familiar with these screens, but if I have 120v to the control power terminals is there any reason the screen shouldn’t light up when we touch it? It is entirely unresponsive.
They say in the past. For no explained reason, the screen would just black out in the middle of operations. If they tapped the screen a bunch of times, it would lighten up again.
Note: there is something weird with their control power. I have 120v between line and neutral. But I have only about 60v from line to ground. There is about 60v potential between neutral and ground. This does not seem right, but would it cause this hmi problem?