Allen Bradley PID CONTROL using Micrologix
Rogertms
Jun 2013
Puchong
I would like to ask about the allen bradley on how to use the pid block in the programming, the software i use is rslogix500 and model of plc is 1762-L40BWA
with expansion I/O IF4 and OF4.
first question, what is the raw value on the analog input and output if i use pid block? is the raw value range from 6241 - 31206 or 0 - 16383?
second question, the pid value of P I and D must can be tuned at HMI or can be fixed value in PLC programming?
third question, do you have any guideline on how to use this PID in the program?
Urgently wanted to know answer, thank you
See PDF's below for data format values for your cards.
You can write to those value from your HMI or they can be fixed.
See link chapter 19 of the manual.
http://literature.rockwellautomation.com/idc/groups/literature/documents/rm/1762-rm001_-en-p.pdf
But for my application, its not for controlling temperature,
is used to control air velocity flow, if its not enough as set point,
it will increase by using PID , controlled by plc but inverter will do the job.
I have a PIDE set up for controlling a tank level. I've run the autotune on it and it is working fairly well except for one thing. No matter...
2,290
Dear all, Please help me out in configuring the PID instruction CCW.
10,553
I am using PID first time in Allen Bradley.I have to Tune a PID on the basis of Pressure Transmitter.I have 3 pumps and pumps will run/stop...
1,670
go to work on this again this morning. I have attached the file and have a question that i can not figure out. When monitoring the temperature i...
3,542