Allen Bradley PIDE Control for flow control
BMLLER6758
Aug 2006
Kiel
93
Hallo Everybody,
Did anybody from you had a sample how to do pump control with flow sensor ???
I only did temperature control with pide yet.
But when I program the pump control the same way the output of the pide get to zero when SP = PV.
So the Motor start...Stop...start...stop...start... stop and so ono_O
Regards and hanx in advance
MERRY CHRISTMAS EVERYBODY
Well, if you mean PID controller, that's a bit odd. I never really heard about this before. Integral component of controller will provide controller output that will remove offset error (read articles on www.controlguru.com). This way, in order to keep PV = SP there will be some controller output or CObias as described in above mentioned articles.
It would be good to provide more details so we can help more.
Cheers!
What are the parameter settings in the PIDE. It sounds like you only have P active and zero value for I.
Flow PID
It seems like you are using the PID to start/stop the pump thats not the way to go, the pump should run continuosly.
You can control the speed of a VFD or position of a control valve with the PID
Roy
If the pump is positive displacement, a VFD usually works well, you can also install a flow control valve that recirculates material back to the source. If the pump can be dead headed for brief periods, you can also install the flow control valve directly to the discharge of the pump.
If the pump is the centrifugal type, you can use a VFD to control the speed, but I have found the response is not linear. You would have to use the pump curves to compute a none linear controller.
I've read 1756-rm006 and I can't fully understand what the difference is between manual and operator control mode. I'm used to "auto" and...
4,133
This might seem like a dumb question however I can't see the difference and can't test it as I don't have an allen bradley PLC available. In the...
25
10,486
Hi Guys! I'm having problems getting the AB PIDE block to actually regulate anything, it seems to be the same problem everytime I try to use one...
23
6,892
367
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
93