Allen Bradley Tag/Alias Question
sjepps
Aug 2016
Virginia
Gentlemen,
I've got 33 of these drives that I'm installing. They're all based on generic ethernet modules so once I create them it produces the tag structure seen below:
What I would like to do is create a generic alias(?) template with comments so that I'm not having to add comments to each drive's words/bits. I would like for it to be a datatype but I don't believe that is possible? Each of word 0's bits are individual command references while the other 9 words are specific references.
What would be the best way to go about this?
I can't tell if the image actually shows. Work blocks most image hosts. Here is the URL:
http://d16i.imgup.net/uncoiler_t9a45.jpg
If you add descriptions to the base Tag in the Controller Tag Database, a tag that is Aliased to that tag will inherit the descriptions.
That's probably the simplest way to go ahead and Alias directly to the INT[x] array.
If you create a User-Defined Datatype and a Tag with that datatype, you can Copy the data from the generic module INT[x] array into and out of those tags. That's typically how I do it, in "Input Handling" and "Output Handling" subroutines. I prefer to use the Copy Synchronous (CPS) instruction to avoid any issues with asynchronicity.
This is how I've done it in the past:
http://q36i.imgup.net/2016-08-1806b0.jpg
Out of the 33 drives, there are 2 types, so 28 are one type and 5 are the other.
I guess if I created a user defined data type I would need to create 16 bools followed by 9 words and use CPS to populate them. That way I could add the comments.
It might be simpler just to export all of the tags to excel and update them from there? I was just hoping to use something that linked them all together.
yes, but instead of test you can write real info like "speed_ok", "healthy" for instance, and then use cps or cop to update, either inputs or outputs.
In your case you have to create 4 UDTS only, since you have only two different kind of drives. Two UDTs for inputs and two UDTs por outputs.
Hey all, I'm doing a more standardize version of one of my programs and organizing things into UDTs and whatever else I can do to shrink the...
422
I'm looking for someone who is more experienced than to bail me out of this mental thought experiment. I am moving away from programmed alarming...
978
Hi All, Good day. Just want to know if you all have an idea on how to convert a Bit address (Local1:I.Ch0Data) from Allen Bradley to Modbus...
1,062
Trying to export my tags to a CSV, according to the help file just select the tags and copy then paste into excel, this works for local variables...
2,474
I'm using the Tag Generation option in KEPServerEX with an Allen-Bradley ControlLogix 5500 Ethernet PLC. It's created some 75000 tags and we only...
2,467