Got an easy one for the experts. I'm new to RSLogix and Allen Bradley and I want to set a timer value via a HMI. I would do this by writing a constant value to say N7:0. However the 'Preset' word only takes a constant and won't accept N7:0. I'm use to Mitsi where you can just assign a Data Register to the timer. How is it done in Allen Bradley?
Cheers
It's also a good idea to check the value from your HMI for limits before moving it to the timer preset. The "LIM" limit instruction works well for this.
Mickey makes a good point but fails to say why....
Allen-Bradley timers have a heart attack with negative PRE or ACC values - major fault....
Sometimes HMIs and PLCs don't speak the same numerical language, and putting LIM checking in is necessary to stop a PLC from red-light faulting.
Min/Max values for A-B timer presets.....
PLC5/SLC - 0, 32,767
Logix5000 - 0, 2,147,483,647
Any value above the "max" quoted above is seen as a negative value, so the PLC will fault/stop