Per your PM, here is some alternating logic that works, and is optimized to use only normal relays, no latches or one-shots. (The one-shot function is wrapped up into the alternator logic).
One-Shot Relay needs 1 NO contact.
P1/P2 Toggle Relay needs 2 NO, and 2 NC contacts.
Stop Float Switch needs 1 NO, 4 NC contacts
Lead Float Switch needs 2 NO, no NC contacts
Lag Float Switch needs 2 NO, no NC contacts
You can probably use your 10 on-hand DPDT ice cube relays for all. You could use 2 relays controlled by the Stop Float to increase the number of NC Stop Float contacts to 4.
If the Lead and Lag Float Switches only have 1 contact, use a DPDT realy for each of those also.
This relay-oriented version has the advantage that the Lag Float does not interfere with the altenator function.
One-Shot Relay needs 1 NO contact.
P1/P2 Toggle Relay needs 2 NO, and 2 NC contacts.
Stop Float Switch needs 1 NO, 4 NC contacts
Lead Float Switch needs 2 NO, no NC contacts
Lag Float Switch needs 2 NO, no NC contacts
You can probably use your 10 on-hand DPDT ice cube relays for all. You could use 2 relays controlled by the Stop Float to increase the number of NC Stop Float contacts to 4.
If the Lead and Lag Float Switches only have 1 contact, use a DPDT realy for each of those also.
This relay-oriented version has the advantage that the Lag Float does not interfere with the altenator function.