Thanks for the vote of confidence, but my version is as only as accurate as the information provided (Garbage In results in Garbage Out).Show Lancie the required project so that he can do it for you
Yes, if the lab PLC is set up like that and that is where your program must run. I think he probably did not realize that he would get anything other than the Lab set-up, when he asked YOU to make the I/O assignments! He probably realized how difficult it was going to be to grade all the programs with each having a DIFFERENT set of I/O.The I/O's is what I think he meant by the requirements not being met. I assigned the wrong cards to the wrong slots.
Meaning that when the Selctor is in OFF, neither the Auto or Manual contacts are ON, and when in in Auto, only the alternator function controls the starting and stopping of each pump. Because your Output list now does not include any contacts for the OFF function, then it is an "implied" off and defined only as when both Manual and Auto contacts are open.When in manual mode an operator will be able start and stop the pumps.
Slot 2 input 0 will be pump 1 stop.
Slot 2 input 1 will be pump 1 start.
There are a few other things that you have overlooked, such as the technical details of the Manual Selector Switch and how the Start and Stop buttons ONLY have to work in Manual mode:
You are not required to use any analog inputs or do anything else with them. Your one and only input from the Pressure switch is a digital on/off input I:1/4. When it goes ON, the pressure has dropped to below 25% of maximum pressure. Because he doesn't say how long I:1/4 will stay ON, you must use I:1/4 with a One-Shot function to activate a "Pressure One-Shot" internal bit for 1 PLC scan. Then use the "Pressure One-Shot" bit to trigger the alternator logic. Use the alternator that you already have.
Don't forget the requirement for drawings of the Input and Output Modules, and a list of your Input functions and Output functions.
Also you need to add the alarm lights for each pump. No specification was given about HOW LONG to leave each alarm going. I would use a 5-second timer to turn it off, as shown in this partial cut from the final program.
Other items that he doesn't list on his Output list are the lights for the lighted pushbuttons. I assume that these are hard-wired in the lab, so that no PLC outputs are needed. If they are NOT hard-wired so the lights go on when the buttons are pressed, then you will need to add PLC outputs and logic for those also.
PS: For the two Pump 2 rungs, both the B3:0/3 Alternator contacts will be
reversed.
additional,
I think the above requirements mean this: In Auto Mode and I:1/4 goes from ON to OFF, then either Pump 1 or Pump 2 will start automatically (without a Start Pushbutton being manually pushed).When in auto mode, one will run, while the other is in standby.
The pump that is started first in automatic will make the other pump its standby,...
If the pressure were to drop below 25% [I:1/4 goes from ON to OFF], then pump 2 would start automatically, and pump 1 would shut-down and an alarm would sound.
Slot 1 input 4 [I:1/4] will be pump discharge header pressure switch (opens at 25% of Pressure).
hope OP get some idea from ours example programs,
select the manual switch will active the pump without PB Start and if select the first auto switch it will become first run and second select for auto switch will be standby pump.
Yes, if this sentence was not in the requirements: "When in Auto mode, one will run while the other is in standby." "Will run" has the meaning of starting without any manual motions required. If that sentence had said: "When in Auto mode, one must be started, while the other is in standby," then it would be clear that the Start PB must be used in Auto.If select the first auto switch, it will become first run
Do not forget about the other 2 requirements:I have to leave some time to attempt this in structured text.