Hi, I've got a micrologix 1200 and I've written a stepper application following the sample application included with the AMCI 3102 stepper controller ( http://amci.com/plc-modules/plcmodules-1762-micrologix-stepper-servo-controller.asp ).
I will be connecting the AMCI module to a 3 axis stepper driver (I'm only using 2 axis though) from Anaheim Automation: http://www.anaheimautomation.com/ma... DPF72002, DPF72003, DPF72004 Users Guide.pdf
I've taken a picture of the AMCI module pinout: http://imageshack.us/photo/my-images/42/screenhunter02dec060833.gif/
I'm a bit confused on how the hookup between the AMCI and Anaheim automation driver would go...
According to the Anaheim Automation manual, the driver has Clock, Dir (1=CW, 0 = CCW) and Motor On/Off for each axis that must be connected.
My thoughts would be that the output of the AMCI must be connected to the clock inputs direction inputs using AMCI outputs #33-36 in an open collector configuration as shown in the AMCI manual on page 32. ( http://amci.com/pdfs/plc-modules/3102-micrologix-motion-module.pdf )(There is also a differential configuration but I don't think my driver supports that.)
Can someone verify if my thinking is correct? I'd appreciate it.. Thanks!
I don't have any firsthand experience with your setup but I do have an application coming up that may require an AMCI 3102 so I have a vested interest in what you're doing.
I believe you need to follow the AMCI diagram on page 33, with the pullup resistors. Your power supply will need to be 5v, not 12-24v as shown in the diagram, since the Anaheim manual lists logic high voltage as 3.5-5v. The connections will then be:
33/34 to 6 (pullup to 5v)
35/36 to 5 (pullup to 5V)
39 to 7 (also to DC common)
You may have to experiment with resistor values. Start high and work your way down. Values in the range of 1K-10K usually work for these kinds of things.
EDIT: You may not need the pullups at all. After reading the Anaheim manual more closely, I see that "the clock inputs are internally...pulled up to +5Vdc through a 10KU resistor for negative going Clock inputs." I'd suggest making the connections above without pullups and see what happens. Be sure to set the jumpers correctly. :nodi:
Greetings Plcple First post here. Begging pardon in advance. Any help with the following would be much appreciated. A 3 axis program was once...
2,079
Hello, I am running a AMCI SD4840 Stepper Motor drive system with Allen Bradley CompactLogix. Every now and then when a 480VAC motor kicks in on...
594
We are currently experiencing a fault on 1 of the 3 stepper motors, keying mismatch fault. The stepper motor is SMD23E2-240A-M12S. We bought the...
1,362
Has anyone used the AMCI cards for the micrologix plc series? Have some existing machines that have the micrologix 1400 plc and they also have 4...
1,597
Hello, I would like to know if anybody knows how to connect or has experiencing using an AMCI 3602 to an Ultraware 3000 for step direction...
3,905