Analog flow control
billbone
Oct 2010
St Louis
I've programmed discrete I/O control in ladder logic but not analog in or outputs. I have two 4-20ma flow signal inputs that are presently run manually. Flow 1 is a continous flow rate and I want to mix Flow 2 at 2% of Flow 1. Flow 2 has a VFD drive on the pump. Can this be done automatically in ladder logic? We use an Automation Direct DL06 for our discrete I/O.
I am not familiar with the DL06, but assuming you have an Analog Output to either control a Valve or the VFD, then absolutely, it is done all the time. Normally a PID Instruction would be used for this, but I have also used a simple Ratio in some cases. It will depend on your exact requirements. There are a number of members who have experience with Automation Direct PLCs that I am sure will help you if you give them enough information to work with.
Stu....
This is not a problem. Depending on the type of pump for flow two you will need one or control two loops.
The first step is to calculate flow 2 as % of flow 1. If the flow 2 pump is peristaltic or other positive displacement type then all you need to do is calculate the speed that corresponds to that flow and send the signal to the VFD.
If flow 2 pump is centrifugal then the flow 2 becomes a setpoint for a 2nd loop, the flow control loop. In this case you would use PID or another algorithm to adjust the speed of the pump until flow 2 equals the calculated setpoint.
PS avoid duplicate posts!
I've never programmed analog control in ladder. Here is what I'm trying to do. Flow 1 Analog input 1 - (4-20ma)0-50 lbs sec, this input is...
5,050
I am trying to figure out how to take a analog signal (flow) and generate a pulse very 1000 gallon for a flow totalizer on my panel. Using...
4,018
Can someone tell me if this math function is correct to totalize analog flow in a 30 Milsec peridoc task...
1,739
As my confidence grows with working with multiple control systems, I am starting to take more and more on, where before I would just pie it off...
3,467
I have a Flow meter that returns a 4-20 signal and the problem I have is the pump is a diaphram pump so theres alot of pulsing causing my...
19
8,026