analog input example rslogix 5000
yes, the tagname used as "Source A" in the link below is an example ...
http://www.plctalk.net/qanda/showthread.php?p=433023&postcount=2
suggestion: people on the forum will be able to help you better if you'll stay in one thread ... this post is directly related to the questions you asked in the last one ...
no offense intended, but this question - taken along with your previous thread - seems to indicate that you're just getting started with this stuff ... if you'll send me a Private Message with your phone number, I'll call you later today and try to talk you through the roughest parts ... sometimes "talking" works better than "typing" ...
and incidentally, here's a fundamental question that I asked back in that other thread:
what type of RTD are you using - and what range of values will you have for the input channel? ... in other words, 4 mA = what temperature? ... 20 mA = what temperature? ...
that information absolutely MUST be nailed down before you can get this project working ... one size does NOT fit all ...
I will have a pt100 RTD connected to a transmitter which will output 4 to 20 Ma. the two wires from the transmitter will connect to the analog input card 1769-IF4I/A The range will be 4 Ma = 0 and 20 Ma = 100 The units will be deg C.
sorry bout creating new thread you can move this to the old thread if you like.
I think what I need is a element to read the 4 to 20 Ma input converting to 0 to 100 deg C then I want to set alarm points Hi and Low to close a XIC bit that will turn on a coil to energise a relay mounted in a panel which will turn on a strobe light
Dear all, any one can you please send me an example programme in S7 300 plc in which 2 analog inputs are read and compared with a preset value (...
14,344
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,146
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
260
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
120
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
88