Analog input not showing true indication
tomalbright
May 2006
Gonzales, LA
691
I have a Ktek level meter, AT26. Yesterday, for some odd reason, the meter failed - as in, no longer shows the proper level. To date, I have changed the transmitter, the analog card (1756-IF16), and the fuse holder just for luck.
voltage = 24V.
current in runs the full range of the 4-20ma scale.
scaling for the meter is 60"
PLC scaling is 12-72"
Simulating an input at the PLC shows the true reading (12-72") for 4-20ma
No matter what I do, I can't get a reading of over 18". I can't figure out how I am losing the signal. I measured voltages at the terminal strip, getting the same thing as another meter right next to it. I'm thinking a voltage problem, but it all seems to check out.
One possibility is the ranging is reversed, but still, with 19ma in, I expect something on the PLC toward the high end.
I'm confused. Any ideas?
Sounds to me like you've eliminated about all possible culprits except the wiring between the instrument and the PLC. Have you tested the copper at all? A corroded connection could certainly limit the current flow.
Bill
Yeah that's a thought. There's lots of wiring between hither and yon. I'm still confused about getting full scale at the terminal strip; it could be a voltage problem with the wiring even though it all "looks good". I'll check.
Hi All, I have wired up plenty of sensors and plenty of digital things over my time. However my exposure to analog cards and sensors is very...
2,576
I've got this 1756-IF8 card configured for 8 single ended inputs as shown below, but none of the channels are read real values (about 4 ma in the...
2,573
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,208
285
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
136