Analog Loop Calibrator

+1 I have one of these, use it for testing and checkout purposes.

Currently in a security line at IAH, but am pretty certain you can change it to .1ma increments as well. You can also adjust the calibration counts too. Would have to check on Monday.
 
+1 I have one of these, use it for testing and checkout purposes.

Currently in a security line at IAH, but am pretty certain you can change it to .1ma increments as well. You can also adjust the calibration counts too. Would have to check on Monday.

would be great if you check it out. Also it says voltage increments are 1V. Maybe just a typo. They might be 0.1.
 
I was actually thinking about this initially but the accuracy of this is 1% and current increments are 1mA
The one from the Automation Store is actually does 0.1mA and 0.1V increments
Webpage may be little outdated - 0.1 was added few months ago.

And its more accurate than 1%.
1% is worst case scenario.
It's usually +/- 0.02mA or better.
 
Last edited:
Fluke 773 is very nice but expensive. Its great feature is its mA clamp which means you dont have to interrupt the current loop.
 

Similar Topics

Good Evening , I’m getting ready to integrate a Mettler Toledo IND 570 into a ControlLogix PLC , Analog 4-20 ma input card 1756-IF16 . I’m...
Replies
6
Views
2,338
If I connect a 4-20mA output from say a magnetic flowmeter (4-wire device) to a PLC AI module (CompactLogix) and to a digital display on the door...
Replies
5
Views
1,636
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
23
Views
638
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
75
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
153
Back
Top Bottom