Lose Analog Loop without PLC Power?
crimson75
Dec 2010
CT
If I connect a 4-20mA output from say a magnetic flowmeter (4-wire device) to a PLC AI module (CompactLogix) and to a digital display on the door in a loop and the PLC loses power will the digital display on the door read whatever value corresponds to 0.0mA?
i.e.: Does the loop get broken when the PLC AI module is no longer powered?
Thanks all.
if the loop is powered from separate power(this is recommendable), so the instrument will have power, the display will work too.
please check the maximum resistance of the unit. some display take 10 Volts.
Thanks all.
If the flowmeter is powered by a different source (true 4-wire device, 120vac, 24vdc...) and the input card is a 1769-IF4I you should not loose the loop signal to an external meter. The card has a 249 ohm input impedance internally. Check to see if the flowmeter signal is wired to Chx+ and (Chx_iRtn jumpered to Chx-).