Analog Output from 224XP help
nehe bhimaji
Apr 2007
Dadra And Nagar Haveli
183
Dear all
Can anybody help me for S7 200 Analog Output
My Problem is , In Catlog the type of inbuilt Analog output (224XP Cpu)is +/-10V or 0 - 20 mA.I require -10V to +10V .As i force 32000 from Microwin 4.0 to analog output there is 10 V output fine,but as i force -32000 thre is 0V output at the output.Please point where i am wrong?
Nehe
Inbuilt analog output of CPU is designed to give just 0 to +10V from 0 to 32000 counts.
-32000 won't give you -10v from CPU AO
If you want 0-(-10v)then go for EM modules or DC/DC converter.
OK give a try by changing the polarity of your wires from analog output.
I wonder how to program the analog output to give for example 15mA out.. Wich value must i send to AQW then??
2,615
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
332
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
91
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
115