anlog output

mo_eng

Member
Join Date
Jul 2008
Location
TEHRAN
Posts
54
hi all
i use a analog output module +-10 volt but i need 0-10 volt for control valve actuator
can i exchange output(+_10 volt to0-10 volt) in plc softwear?
my base unit is twido and my analog module is 2HT
 
I'm not familiar with the Twido, but it would apear a quick solution would be to limit your output to 50%, corresponding to 0 VDC. You would loose resolution, but the output probably has more resolution than the valve anyway.
 
hi all
i use a analog output module +-10 volt but i need 0-10 volt for control valve actuator
can i exchange output(+_10 volt to0-10 volt) in plc softwear?
my base unit is twido and my analog module is 2HT


As stated, you can simply set up your scaling for 0 - 10V... If you desire, you could also add a line of code, that if the output is less than zero... Move zero to output.

-MUR
 
in S7-200 Plc for example,if i want 10V output i move 32000 value in the output address,if i want 5V than 16000 and 0 than it should be 0.
i dont know how you can vary the output in twido.
 

Similar Topics

I'm currently starting up a system in China with a 1769-L36ERM and 3 remote panels with point IO rack connected with an AENTR. I have few digital...
Replies
4
Views
2,025
- Controllogix L61 PLC - 1756- IF8 Analog Input Card set at RP1 of 75ms I need to Totalize flow from a Mass flowmeter. Analog 4-20ma output from...
Replies
6
Views
3,248
how to configure RTD PT 100?? PLZZZZ give some good advice that how to begun programing beacuse I am very new in field of PLC.
Replies
6
Views
1,715
Dear friends, Presently we are commissioning S7-200 CPU 226 based machine in our soap plant. The configuration is CPU 226 + EM235 + EM232 + EM...
Replies
2
Views
7,789
The GE90/70 choice of programming functions is limited they don't even have a simple scale block. Amazing. With the limited functionality how...
Replies
4
Views
6,120
Back
Top Bottom