ASi
grantg
Jan 2011
Inidana
I am adding a device to our network of discretes. I did address the device. it comms through trunk and drops. we have 3 devices on one drop box. do I address the point on the drop box, too? same as device/slave address #? How do I map the I/O in control logix 5000? current I/O bits look like ASi_Net2_Input.Data[0].11, etc. How do these #'s coincide with the ASi network, trunk and slave #'s? Any help is appreciated.
For us to help you will need to tell us what modules are between the cpu and the field device.
Without that info I can only suggest you look at the existing I/O table and see what bits flip for the current I/O devices.
Get the manufactures user manual and give that a read. Most likely they will also have an example program or two that will give you the basics of how they specify I/O.
The drop box is typically just a splinter and has no address associated with it.
bihl*Wiedemann AS Interface Master module in Control Logix 5000 rack. Two network/modules in the rack. Downstream in an AC1216 AS-I power supply going to an AC2215 AS-I repeater to an AC1218 power supply the to the Stonel FBP08007 drop connector box. Three devices connected to the box. Just want to know how to ID and program a newly added device (discrete) to my I/O PLC programming and how to get the new slave ID's for the AS-I module in the PLC rack. I know what slave/address to use to address the device itself.
Check out manual
http://www.ifm.com/Images/Files/ASI_Tools/ControlLogixBPManual.pdf
Page 11 shows how byte swapped mapping works (ASi looks like it comes from Siemens)This will show you how slave number etc relates to mapped IO Tag ASi_Net2_Input.Data in your program
I have a spreadsheet set up so slave adresses show up in order, but I/O adresses are byte swapped
Page 79 shows how to get new slaves into configuration
I hope this helps
The Stonel (http://www.stonel.com/FieldLink/IAS/105056revA.pdf)looks to be just a junction/terminal box, so addressing is not relevant to it.
The IFM AC1216 & AC1218 are just supplying power to the AS-i network. The IFM AC2215 is just a repeater, no addressing for it.
As mentioned by others, the bits in the I/O words are not linear, they are swapped, at least for the IFM interface. And there is more than one bit per device.
Most likely you will not have add any I/O address as the array ASi_Net2_Input.Data should have been made large enough to cover the maximum number of devices that can be connected.
You should know the AS-i addresses of the existing devices and looking at the program & tag array, see where they are. So you can find out the # of bits/words between them that are used for PLC I/O. And then go from there for your new device, since you know what AS-i address you're doing for it.
Hello all. I am trying to communicate to an ASi gateway from my CpLX (L16ER). I am able to ping the gateway and it replies. I configured the...
55
How can I integrate my S7-300 Simatic with the IFM AS-i Master AC1335 and its slave IOs, such as 2411 and Airbox 2041, into Simatic Manager?
140
I've been called to a site to assist with an ASi fault. The line has been down for a couple of weeks following a failure of the ASi power supply...
1,336
Hi folks, I had trouble with door switches on a machine I was working on today. What first appeared to be as a simple reed switch turned out to be...
760
Working on a Pepperl+Fuchs VBG-ENX-K20-D-EV24 Looks like to many hands in the mix. Everytingwas played with. I am new to this but restored...
1,208