You'll probably have to talk to the OEM. They should provide you with the list of registers to read/write. If that's been given to you, then I imagine it's "configured".
When Atlas-Copco installs the gateway they should have given you a document with the specific registers of that gateway. If you had a copy if the software used to configure the gateway you could do it yourself.
To quote an old email i dug up from an Atlas Copco service technician "Also attached is the rather exhaustive address list for a Mk4 elektronikon controller as it applies to the Mk4 controller. In the attempt to cover every variation... the guide covers different types of equipment and their nuances along with the standard registers. In particular Sections 2.3.2; 2.3.3; & 2.5.1.2 may be of particular interest.
The detailed address report would look something like this:
AC MkIV reporting file
Monday, March 02, 2015
Modbus IO definition
Analogue Inputs
Compressor Outlet
Pressure - mBar
Status : reg 1, Value : reg 2
Dp Air Filter
Pressure - mBar
Status : reg 3, Value : reg 4
Oil Pressure
Pressure - mBar
Status : reg 5, Value : reg 6
Intercooler
Pressure - mBar
Status : reg 7, Value : reg 8
Element 1 Outlet
Temperature - 0.1°C
Status : reg 9, Value : reg 10
Element 2 Inlet
Temperature - 0.1°C
Status : reg 11, Value : reg 12
Element 2 Outlet
Temperature - 0.1°C
Status : reg 13, Value : reg 14
Compressor Outlet
Temperature - 0.1°C
Status : reg 15, Value : reg 16
Oil Temperature
Temperature - 0.1°C
Status : reg 17, Value : reg 18
Cooling Water In
Temperature - 0.1°C
Status : reg 25, Value : reg 26
Cooling Water Out
Temperature - 0.1°C
Status : reg 27, Value : reg 28
Digital Inputs
Emergency Stop
Status : reg 201, Value : reg 202
Remote Start/Stop
Status : reg 203, Value : reg 204
Remote Load/Unload
Status : reg 205, Value : reg 206
PB1 open / PB2 closed
Status : reg 207, Value : reg 208
Overload Motor
Status : reg 209, Value : reg 210
Starter Feedback Contact
Status : reg 213, Value : reg 214
Electr. Condensate Drain
Status : reg 217, Value : reg 218
Counters
Running Hours
Value : reg 301 + 302
Loaded Hours
Value : reg 303 + 304
Motor Starts
Value : reg 305 + 306
Module Hours
Value : reg 307 + 308
Load Relay
Value : reg 311 + 312
Special Protections
combox-e and control logix
p
Pretty well got the code running now. I dont have live compressors attached to the Commbox, but the responses from the Commbox make sense.
It ended up being quite a complicated little program, especially when there are multiple compressors on the Commbox, and my obsession with making code that is non dependant on the data (ie making it very easy to add new data in future)
Once i connected with the commbox using the information given above, the documentation actually made quite a lot of sense and was pretty useful in understanding the packet structure that the Commbox uses. I just wish that they added that as a section in the document given by Atlas Copco.
if anyone has problems in future with this bit of gear, send me a PM and i should be able to give you a hand.
Hello, please give me example of code, my mail is
[email protected]
hi everyone, i work with CPU S7-300 and gateway Combox-P gor get data from Elektronikon. The project work ok ,but since 5 days ago in one of the compressor i received an error in the data record, specifically error 1 ''NODE ADDRESS NOT FOUND", i check the cables, i restart the combox-p and elektronikon , the error 1 keeps happening, what can be? thanks
Does anyone have some sample code for communicating with an Atlas Copco Combox-E via a ControlLogix PLC? A friend of mine at a plant in Louisiana...
7,189
Hi All, Currently I'm working on a project which requires establish the comms link between ComBox-E and ABB AC800M PLC. We have many ABB AC800M...
5,988
I have a problem with combox-e. without 1756-CNBR,it's OK that plc connect with combox-E. plc: 1756-L61*2; 1756-ENBT*2; 1756-CNBR*2 1757-SRM*2; in...
3,425
It was hard trying to find the software ECT for this drive. Finally, I found it but since it is very old it is not intuitive at all. Is there a...
108
Hi Guys, I'm looking for a download for the ToolsTalk software for atlas copco controllers (power focus). The laptop that had it died and of...
3,168