Automatic sequence in S7
pauly
May 2002
South Wales,U.k
244
I have a job utilising an S7 400 plc which requires a no of automatic sequences to occur.I have some nice timing diagrams from the customer but I am a little unsure of the best way to approach a sequence in S7, weather the sequence steps are based on a counter value, values in a data register or function block, any ideas would be very much appreciated.
Siemens can supply Graph 7 which integrates into Step7. Graph 7 allows you to define your sequence steps/transitions etc and you can view them graphically during test/debug. Note that the end customer will need Graph 7 if they need to investigate/tune any sequences !
Alternatively you could implement the sequence using ladder logic and use a DB to store the steps/actions etc. (I prefer this method for the limited sequence work I have done as is does not rely on the customer needing Graph 7)
I always use the SR approach to translate from Grafcet (or SFC, or Graph) to a ladder program. Every step is a SR memory. The S is determined by the previous step AND the transition conditions, the R is determined by the next step. Works like charm on every PLC, even if the brand never heard about Graph.
Once you're used to it, it's fairly simple to adapt the same principle to relay logic or even pneumatic sequencers.
Kind regards,
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
89
Hello everyone, I'm having trouble solving this one and was hoping someone could help. I have a AB CompactLogix L16ER PLC connected to a AB...
591
Hello everyone, I was hoping someone with a lot of experience with Automatic Device Configuration would chime in with any of your thoughts on this...
1,841
Hello. At my job I get from clients lists of their inputs and outputs (hundreds of them) and what they want the program to do. So I have to type...
1,348
For some reason the PLC (TM221CE16T) saves all Memory Bits and Memory Words automatically so after a cold restart it restores not only %MW0 to...
18
4,843