Averaging in GX Developer to reduce spikes
Densam
Apr 2005
113
Hi ;Configure A1s64AD card in slot 3 is as attached. This is averaging count. my signals are coming in at channel 3 and 4. There are spiking so i wanted to smooth out. Looked at the code now i want to adjust i am not sure how to go about this. Any help will be great. I have checked the wiring and grounding. Changed the damping in the transmitters. See attachedGX developer A Series.jpg
trends.jpg:mad::mad::mad:
Fixing the problem in software should be a last resort.
I would find the source of the spikes. Do this using the divide and conquer technique. For instance I would get a scope and measure the noise at the sensor first after disconnecting the down stream wiring. This way I would know if the noise is coming from the sensor. Then with the sensor still disconnected I would put a resistor equivalent to the output impedance of the sensor across the wires and see if noise is being induced on the wire going back to the PLC.
Hi, I have a bit of PLC experience in Siemens and have unfortunately been blessed with working on Automation Studio and B&R which has been a big...
1,365
The PLC code calculates oil flow rate and outputs it on D420. It is represented on the HMI as a vertical bar. Problem is that the operator says...
33
4,940
Hello, I am working with a laser encoder that is providing the speed of a fiber strand to our AB 1756-L61 PLC. In order to calculate the amount...
3,153
Hi, folks. Thanks for taking the time to read this. I need to average 5 numbers, they being an accumulated value (mSec) from a timer. My director...
19
5,649
Hi folks, First and foremost, credit where credit's due, thank you daba for the averaging sample provided in a separate post back in 2013. I've...
3,918