I have a Conveyor System Running Balluff Remote Ethernet blocks
Topography has ethernet going through Master-2 to Master-1
(BNI EIP-502-105-Z015)
Master-1 has 4 slave blocks (BNI IOL-302-000-Z012)
Slave Block #4 on this has what appears to be only the top half of each
M-12 I/O connector working.
I changed out slave with new one and get one light for the only input associated with this slave and outputs are not working.
I will swap back original and see if I get back to 1/2 working.
I can Ping master and look at its web page.
Does the RS5000 (Compact Logix 5380) set everything I need except IP?
or do I need to address something ? I dont see anything in the manuals.
I changed some bits in the program to get it to run loads through this Zone and move to the next but have been running like that and I was hoping new blocks and cables would find a cure.