Basic PLC with IO-link, does it exist?
ggc
Apr 2007
Queensland
86
As per the title, does anybody make a basic PLC that directly supports IO-Link without requiring a fieldbus and remote IO modules?
I know it goes against the basics of what IO-Link was designed to do, but I've got an application that requires 2 * flow sensors, a stack light and some pushbutton control, getting fieldbuses involved for a simple application seems like overkill.
Or is it going to be easier to stick with something like a Automationdirect Click Plus,Modbus TCP and a remote IO module like an IFM AL1342?
1) Lots of PLCs have fieldbusses integrated in, so adding a remote IO LINK master on Ethernet or whatever isn't really all that hard.
2) I know of some that can do it via IO cards, which could be in the PLC rack. From Siemens, the S7-1200 family has the SM 1278 4xIO-Link master.
3) personally, I wouldn't choose my PLC based on this, unless you find a solution for a PLC you're familiar with or you're going to build a lot of systems. If this a one-off, you'll spend more time learning a new PLC platform than you would save by simplifying the system.
I think that going for a PLC that can integrate IO-Link master modules directly without going via a 3rd party device is the better solution. If (more like when) things don't work out as expected, it is difficult to get support when it is a mixture of devices from different suppliers.
So in my opinion, the S7-1200 mk42 mentioned would be the obvious simple and 'basic' solution.
For a basic "PLC" with some IO what about a Siemens LOGO you get a few In/Outs and an analogue. Or as said above the S7 1200 range,
You could use a Phoenix - "PLCNext" setup but this would use field IO.
Or, for a small "home project" What about https://aceautomation.eu/ falls into the cheap and cheerful category, but may not give you the connectivity of siemens or Phoenix
Wago PFC100 with a IO-Link card is an option. But honestly IFM Masters are about the same price as a Card. I just use the PFC100 and IFM AL1920 Masters
Edit: NVM looks like they discontinued the Wago 750-657. Probably because no one wanted to buy it when a IFM Standlone master was the same price.
I found this from Siemens: https://mall.industry.siemens.com/mall/en/WW/Catalog/Product/6ES7278-4BD32-0XB0
You can try and spec a S7-1200 for your application, and this would just be an add-on card.
The Siemens S7-1200 with something like the ifm Al1400, is an obvious way to go if you want to use an io-link with a basic plc.
You can have a Beckhoff CX PLC (technically it is a small IPC) with a 4-channel IO-Link master terminal EL6224:
https://www.beckhoff.com/en-us/products/i-o/ethercat-terminals/el6xxx-communication/el6224.html
There is a great variety of the CX controllers, from the smallest/cheapest to the pretty powerful: https://www.beckhoff.com/en-us/products/ipc/embedded-pcs/
This might be a good solution if you are familiar with or not afraid of learning IEC 61131 programming stuff; primarily the structured text part, since the ladder part is somewhat limited and awkward.
Create ladder logic program to count 4 on pulses (not using a counter) and then turn the output on if the on pulse input signal can look like the...
105
36,466
Hi Friends, I'm making a PLC operated chocolate vending machine, using a CLICK Basic PLC (C0-00DD2-D) which has 2 x RS232 ports. I'm also using...
1,535
hi all, which AB PLC or module that runs on BASIC language? thanks
3,559
Hi all, First time posting. I'm an new journeyman electrician from Canada trying to move to the industrial side of things. I have so far written...
5,836
Hello all, i am planning to start basic plc and programming classes online if anybody is interested mail me
1,400