Beckhoff CX9000 Run-Time system already in use error
jackleblack
Nov 2013
Canada
Hello,
I am trying to open the PLC project directly from the Beckhoff CX9000 (Screenshot 1) to do a backup of the project, because we don't have access anymore to the project files. However I am greeted with the "Run-Time system already in use" error when I try to open it from TwinCAT PLC Control (Screenshot 2). I have full connectivity inside TwinCAT System Manager in Run Mode with the PLC, so the communication is not an issue I think.
Here's the PLC in question if you need any additional references (Screenshot 3).
I tried looking around for that issue on other forums, but I have come to a dead end.
Does anyone know how can I fix this error?
Thanks in advance
if project files are missing you do not have a good possibility to get it good anyhow, you can upload the files to the PC, but that is just for backup when system fails.
ask the supplier for the project, this way you can change something if needed.
I was hoping that Beckhoff was somewhat similar to Allen-Bradley, where you could upload the program from the PLC and easily edit it that way in RSLogix (at least that's how our SLC 500 works).
If I understand it correctly, even if I do manage to get the PLC program off Beckoff, I won't be able to do any edits to it?
Thanks for your reply shooter
There is something similar to it that is referred to as downloading the source code. But it is up to the programmer to explicitly download the source or configure the program to download implicitly.
If by chance that was done, then you can upload by going to File->Open->PLC
The "RunTime in Use" generally means another computer is already online with TwinCAT.
Hi, I'm working with Beckhoff CX9001-1001 and CX9000-N031. I want to have 2x RS485 modbus rtu, how N031 must be configured in System Menager...
2,693
Heloo, I have problem to communicate with Beckhoff CX9000 PLC and Denon AVR 2313. I want to send commands to Denon receiver from PLC...
3,227
Hi, I have a problem with implementation of Modbus TCP/IP on CX9000. I did install Tc.ModbusSrv.lib in Twincat ( i use Twincat 2.10 v). I'd...
9,813
Hello! I have Beckhoff CX9000 with N031(2 RS-485) module on board and Mitsubishi FRA740 inventor. I need to control inventor with Modbus RTU, but...
4,171
I have a cx9000 that has started up and will not get out of config mode. The power LED is Blue. I have reset to factory defaults, forced it in...
5,188