Beckhoff TC2 ADS Error 1796 writting/reading not permitted
AivisNewBie
Mar 2018
None
Hello all,
I ran in to some trouble.
I created 2 virtual machines to try out ADS communicating One machine is a PLC (TC2 32bit (runtime)), other is (should be) a client (TC2 64bit engineering+ Visual studio adsAPI) that should read/write from/to PLC VM.
1. problem : TC2 64 bit engineering does not find a PLC VM. (i know it is possible to find it (https://www.reddit.com/r/PLC/comments/2mhbjh/help_connecting_twincat_211_plc_program_running/ )but mine does not find it)
2 problem: (bigger one). I can find this VM PLC from other 32bit VM with TC2 32bit, but when I try to "add route" I get ADS error 1796.
I saw one post on this forum about very similar issue(http://www.plctalk.net/qanda/showthread.php?t=89563&highlight=ADS+ERROR+1796), but could not find answer here.
Maybe someone here tried this out and could help me out?
thanks you all in advance :)
For those who are instrested I managed to fix my problems.
2 Problem [Solved]: silly mistake Beckhoff add route requires PC name and password so entering it removes the problem and route is added
1 Problem [Solved]: dont know why but TC2 64 bit (engineering) does not install good on Win 7 (pro), trying this on W10 mashine worked like a charm :)
hope this helps someone :)
I tried to install it again as "Admin" but no luck, the symbol of TC2 (the one that is blue in config mode) is blank on W7 pro (Virtual Machine) :)
Hello Long time lurker. I am flailing around trying to figure out how to implement MODBUS TCP on a W2000 IPC that controls one of my company's...
5,888
Hello all, I've got a problem with Alarm history display and saving to file, I tried to follow example on beckhoff site...
1,889
18
1,020
Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
101
hello, I am using Beckhoff with TwinCAT3 and when I change or add some new hardware or for any reason, there is a mismatch in the real hardware vs...
128
