For the common.. if we are using 24 Vdc , do you usually use the 24V+ or 0v- ?? what about with 220 Vac ?? phase or neutral ?
thanks !
0V- is the common in 24vdc
220vac is usually a phase to phase voltage so there is no neutral. but a typical 120 vac system would have a neutral which would be the common
thanks !
Define 'common.' Do you mean common as it relates to the power supply, or common as it relates to I/O module common or switching N.O, N.C, COM(mon)
We usually use 24VDC and 0VDC for DC power. Some customers want +24 and -24 which is misleading to me, but hey the customers always right.
For 220 or 480 will have L1 L2 L3 and sometimes N if they are using a neutral.
common i refer to the I/O..
24+ and 24- ?? how is that.. are there any power supp that admit that ??
ok thanks for answering.. one last question. When you say +24V and 0V.
You actually have a difrerence of 24V between the + and - of the power supp.
But why 0V ? is the (-) grounded in the power supp and thats why you say 0v ??
Or is it just a naming convention also..
0V is the common naming convention, as it is 0 volts to ground, but some customers, as JaxGTO says, call it -24V since it is the negative side of the 24 volts, but truly -24V would be below the ground and 48 volts below the positive side.
Welcome to the start of a lot of confusion.
It would depend on the devices (I/O module and connected devices.)
For an OUTPUT module, assume that the signal on the COM terminal is the signal that gets switched to the output terminal(s.) What signal is COMMON (connected) to both, the output module and the power supply...
When I say OUTPUT MODULE, I mean the smallest portion of the output module that has an individual (ISOLATED) COM terminal.
Some output modules have multiple COM terminals - the COM terminals MAY OR MAY NOT be internally connected.
Assume that we have these two devices RS4N-DE and RS6N-DE.
They are two of Automation-Direct's offering of small, multi-relay din-rail mountable modules.
They are quite similar, but distinctively different. See discussion of sourcing/sinking.
For the RS4N-DE, you would connect the +24V to the OUTPUT module's COM terminal,
and then the output module would switch the +24V to the RS4N-DE.
In this arrangement, you would connect the 0V to the RS4N-DE COM.
For the RS6N-DE, you would connect the 0V to the OUTPUT module's COM terminal,
and then the output module would switch the 0V to the RS4N-DE.
In this arrangement, you would connect the +24V to the RS6N-DE COM.
I do not have an example of connecting the NEU to COM in an AC circuit.
Some people use GND, 0VDC, COMMON interchageably.
It really depends on the context of the circuit at hand.
Say I have an embedded controller circuit, I may say 5V, 3.3V and GROUND. What I REALLY mean is 5V, 3.3V and 0V.
I like to say 24vdc+ and 24vdc- since the + and - go along with the terminal discriptions on the power supply.
"Common" is just a catch-all term for any conductor that is shared by multiple devices. It could be the ungrounded or the grounded conductor, depending on what the application is.
For example, a PLC input will use the grounded conductor (negative in a DC circuit, neutral in an AC circuit) as the Common, because all of the input channels have the grounded conductor "in common." On a PLC Output card, the ungrounded conductor is common because all of the output channels in a given group will share the ungrounded conductor "in common."
FT, please rewrite this paragraph to include the ability to have sourcing/sinking inputs and sourcing/sinking outputs.
Not all Input modules use the 'grounded' conductor as a common, and not all output modules use the 'ungrounded' conductor as common.
I have a relatively small network but I am having some issues with PowerFlex 755 drives (using the native ethernet card) Faulting with the F926...
223
What's the best way to use lots of MSG instructions in the same program? Both multiple messages with the same device, and other devices. I've read...
1,200
Hi all, We are looking for the best practices when it comes to maintenance technicians having online access to our PLC's. We would like to give...
1,161
I would like to compile a list of all the CX-Programmer PID Best Practices If there is some clever way you have figured out to do something and...
678
Hi everyone. I am very new to TIA Portal, and I come mostly from the Rockwell world. I have a question regarding program structure. For some...
3,577