Best way to add PLC card to running SLC 5/05
smohamed
Mar 2008
ON
108
Morning everyone,
I know this sounds trivial (but I haven't done it in a long time) but what is the best way to add a PLC card to a running program? I have a SLC 5/05 running, and want to add a digital input card to the rack.
I assume I should power down, add the card, and then power back up which at that time the PLC should fault because of the config. Should I update my PLC program with the new DI card in the I/O config and then download to the controller?
Any help would be greatly appreciated.
Thanks!
Here is what I do:
Get online
Stop the machine that it is controlling
Once it is stopped, save the program
Go offline and power down
Add the card to the rack
Add the card to the PLC program
Power up and download
If you put the controller in program when you power up, it will not fault.
you assume correctly. I make a good backup of the program from the SLC, save it as a new name, and add the new card into the i/o config. Gives me a easy way back to square one if something goes wrong.
Thanks, I will have to try it out.
Thanks for everyone's help.
I ended up saving a new copy, adding the card and shutting down then downloading back to the controller. Had to wait for some of the process to come back, but it did work out.
Hello Everyone, I have about 135 controller PIDE loops that I need to add to my Studio 5000 and that means I will probably have to create about...
1,919
I have examples from Logix 500 of how to do a slow increase to the speed reference value, while the operator is holding down a button on the HMI...
1,542
V 10.00.01 Patch 9 I was wanting to make an analog process variable display global object but I guess that is not a good idea. We are doing this...
4,918
Hi, My boss just ask me to convert all add on instructions into normal rungs. Currently, it is add ons in add ons.......... I am just wondering...
2,569
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
498