bitzer compact screw compressor
mo_eng
Jul 2008
TEHRAN
54
hi ll)
i use four compact screw type compressor(bitzer brand) in a chiler and i dont have any idea for capacity control(it has four step unloader)
do you have any experience with bitzer compact screw compressor?
It is quite simple (isn't everything when you know how :))
http://www.bitzer.de/eng/product/list/prod4/dcode/SH-170
See chapter 2. Are you using a frequency inverter ? If so you don't need to use CR1/CR2, only CR3 to unload at startup and CR4 pulsating to return the oil.
If you don't have an inverter you can either use step capacity (25%/50%/75%/100%) or infinite control (by pulsating CR3/CR4 you control the slider).
Usually infinite control provides better accuracy and is good for quick reaction, like regulating chiller outlet temperature.
Step capacity is good for slow response, like regulating on chiller inlet temperature.
Hope this helps!
thank you a lot p.d.l
but can you more explane step capacyty control ?
Have you read the manual? What don't you understand?
logic
i cant understand !!!
i have a four stage thermostat for control four compressor.
now i cant undrestand how can i do that?
i dont have any experience with this compressors.
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
132
What happens if you power up a 1783-MS10T with a Compact Flash card from a 1783-MS06T? Does it work, but with the "extra" ports unconfigured? If...
95
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
135
My PLC is currently running the program and the process is still live. One of my 1769-if16C cards values are all frozen but the card is not...
132
I've blown the Output Transistor on the Output Card of a Compact Logix 1769-L24ER-QBFC1B It says J378. Does anyone know the replacement part...
209