Calculate DC current for AC-motor
aand74
Dec 2005
Deinze
131
I know the nominal AC current of a three phase AC motor, but because I intend to use a drive system with central AC-DC converter and then DC-AC units for each motor, I was interested in how to calculate the DC current that corresponds with the nominal AC current.
At least current rating of motor * 1,42. I don't have experience with systems with central AC-DC converters, but it is logical as it is essentially PWM, and highest value will be the one I'v mentioned. There is also question of start because in that moment the current is much higher.
This is not necessarily a straightforward question. The answer depends on several factors, some of which are how fast the motor is turning, the efficiency of the drive connected to the motor and total bus utilization (which affect average bus voltage). But the most direct method of doing this is to calculate the output power of the motor at the speed of interest, add in losses due to inefficiency to determine power requirement from the bus, then divide by bus voltage. That will give you a reasonable idea of bus current requirement for that axis. This is not necessarily the same as the current required from the power supply since other axes may be generating at the time.
Keith
Hi guys, For the electrical current consumption calculation for a metering pump, does anyone know how to get the peak current & fuse ampere -...
1,914
Hi All, I have to find out how much 17x1,5kW and 3x2,2kW inverters use in inrush. The 1,5kW inverter have needs a power supply capacity of 4,5...
19
5,738
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
18
1,057
Good morning, I have a question. I don't know much about ST yet I would like to calculate the average number of products per hour. how do I do...
22
2,980
Can someone help me with this? I'm no good at SCL - virtually everything I've done so far has been ladder logic. The return value from the...
1,117