can i use PF525 as input unit?
mike3475
Feb 2013
brooklyn ,NY
334
Hi,Guys:
since we used all inputs of the PLC, no any input left for our new project.we have a few PF525 connected with Ethernet, can we use it for input unit?
thanks!
Hi,Guys:
thanks!
Any reasons you can't use remote IO?
Some pretty good systems that run over ethernet and are rated IP67 (or better) and can be mounted in the field.
Parameter 14 is the Dig In Status, and the first 4 bits monitir terminals 5 to 8.
P14 bit 0 = terminal 5, and so on.
You would need to use a datalink to get the status to your PLC, note the datalink values cannot be changed if you have an established I/O connection to the drive.
Alan
You can monitor up to 4 parameters on a 525 drive at the RPI you have set for the drive. This is set in the module configuration where you select the HP, revision, and keying options. You could potentially use this for IO. If the IO is not related to drive function I would highly recommend adding a card or remote IO solution since it would be quite confusing to troubleshoot.
I seem to be on here often lately but cant find specifics about my situation I am trying to control the drive using both ethernet and analog(for...
766
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
1,043
Hello all, New to this site - I am adding a new conveyor and using a powerflex 525, though the rest of the drives operating this line are...
1,314
I have a (*) PowerFlex 525 being supplied with 400VAC, 60 cycle, 3-phase. This is not a type-o, this is accurate. Now, the drive clearly states...
1,227
Has anyone had any success using a PanelView Plus to directly control a PF525 over ethernet, I tried to use the file provided with TechNote...
1,074