Can someone help me with a PLC2?
Psymon
Jul 2004
Wisconsin
111
Alright I've got a fairly small PLC-2 program printout that I've converted into a PLC-5 program. A couple of quick questions on the instructions though:
1. Does someone have a bit level breakdown of the TON instruction for the PLC-2. Specifically what bits 15 and 17 signify, since they aren't referenced the easy way (TT, EN, DN) like a PLC-5.
2. I'm assuming that the CTR command is the same as a RES command?
Thanks fellas.
Jay
Psymon,
15 - DN
16 - TT
17 - EN
They are the same as a PLC-5, just octal instead of decimal.
(i.e. If you enter T4:0/13 in a PLC-5, it will change to T4:0/DN)
Twenty-one years ago !
From my vintage Mini PLC-2/05 Reference Manual, Publication 1772-6.8.6, Oct 1984. Page C-9
The counter word address, XXX, is assigned to the counter accumulated areas of the data table. To determine which addresses are valid accumulated areas, the most significant digit in the word address must be an even number.
Bit 14 is the overflow/underflow bit
Bit 15 is the count complete bit
Bit 16 is the enable bit of the CTD instruction
Bit 17 is the enable bit of the CTU instruction
The words address displayed will be 3 or 4 digits long depending on the data table size. When entering the word address, use a leading zero if necessary.
CTU = Up Counter
CTR = Counter Reset (resets bits 14,15,16,17 and accumulated value)
CTD = Down Counter
If a programmable controller controls the operation of a motor, what connects motor control to the PC? A) Line voltage B) I/O device C) Modem D)...
27
7,129
Hi all, Am new here, normally I work on OSAI and Beckhoff systems but I have a problem with some Indramat dkc11.3 drives that all display the...
1,424
i have a project that i need help designing. i go to college but we only get 2 hours a week to work on the computer that has the plc program. i...
2,420
Hi, i uploaded program from Allen Bradley PLC, i need someone to help me elaborate more on this uploaded project will appreciate any help thanks
2,129
Hi Friends ! I'm having a little challenge here, I'm almost done in my conversion project from panelBuilder to Factory Talk. I really need a...
1,587