Canadian electrical code on wire color?
halosome
Dec 2005
bc
73
Hi guys, I've got probles in color on the PLC terminals. what color should be on the low voltage wires? Blue on both positive and negative? and what color should be on 120vac input terminals of a PLC? Red or yellow?
Thanks, and please tell me where in CEC can I find the answers
The industry I'm in uses:
blue - low voltage DC
blue & white striped - DC common
red - low current 110VAC
white - AC common
black - high current 110VAC or larger voltage AC
yellow w/ red strip - remotely powered AC (interlock)
yellow w/ blue stripe - remotely powered DC (interlock)
purple - jumper between two wire numbers
Your mileage will vary and this is definitely facility dependent but pretty close.
PS: this includes customers in Canada
Mike technically NFPA 79 is the standard for wiring electrical machinery in the US. I believe the US and Canada will be very similar, if so the low voltage + will be blue and the - will be blue with white stripe. Red would be 120vac, yellow should designate an external voltage source that is not de-energized by the panel disconnect.
NOTE: There may be a slight difference in Canada but since NEC and CEC are supposedly "unified" it would surprise me if there is much if any difference.
I will not go into that debate about NEC/NFPA...no authority..etc etc al. In the US, OSHA uses NEC/NFPA standards as guidelines for their regulations...in many cases they specifically reference them.
wire colour :)
The section you are looking for is section 4 CEC. Section 10 on Grounding covers gound colour and section 16 covers class 1 and class 2 control circuits.
Color Coding of Industrial Control Panels of UL
Thank you guys! I think I've found the answer from UL for Canada. It is said same to Canadian Code and is similiar to jstolaruk's oponion. I believe it is in Canadian Code Part 2,But unfortuanately I don't have one. Here it is:
66.9 Internal wiring of control circuit
66.9.1 the following color-coding shall be employed throughout the panel:
a) Black – all ungrounded control circuit conductors operating at the supply voltage.
b) Red – ungrounded ac control circuits operating at a voltage less than the supply voltage.
c) Blue – ungrounded dc control circuits.
d) Yellow or orange – ungrounded control circuits or other wiring, such as for cabinet lighting, that remain energized when the main disconnect is in the ²off² position.
e) White or gray or three white stripes on other than green, blue, orange or yellow – grounded ac current-carrying control circuit conductor regardless of voltage.
f) White with blue stripe – grounded dc current-carrying control circuit conductor.
g) White with yellow stripe or white with orange stripe – grounded ac control circuit current carrying conductor that remains energized when main disconnect switch is in the ²off² position.
Exception: Leads on assembled components, multiconductor cable, leads used to connect electronic devices, and conductor sizes 20 – 30 AWG (0.52 – 0.05 mm2) are not required to comply with this requirement.
66.9.2 Control circuit conductors shall not be smaller than No. 18 AWG (0.82 mm2).
Exception: Control circuit conductors for programmable input/output and static control wiring are able to be sized No. 18 – 30 AWG (0.82 – 0.05 mm2).
One more question
I have another question: I made 2 cabinet side by side, one's output is another's input. According to the rule: at 1st cabin, I should put red wires, and 2nd, yellow wires.
What should I do?
Through good or bad practices, we use the following in our plant, (sometimes)
Red OR Black = 120VAC hot
White = neutral
Solid blue = +24VDC or -24VDC, relying only on wire markers
Purple = either a pull wire OR -24VDC
Yellow = signal exchange between panels/systems 120VAC OR 24VDC
460 3 phase = Brown/Orange/Yellow
230 3 phase, grounded B phase = Red/White/Blue
Jumpers stick with what ever color their native voltage level is.
I really wish we'd use different wire color for -24VDC stuff that is bonded to ground versus a floating -24VDC system. We have a great mix of each.
Greg
What should I do?
Assuming 120VAC, I would use red in the panel that the power is sourced in and once it makes the transition to the other panel, those same signals would become yellow. And vice versa.
Hi, I am designing an electrical panel for my fourth year electrical engineering project and had a afew questions about the electrical code in...
7,307
Dear members, We were "dinged" during a recent safety inspection for not having an operational door knob on a door that services an electrical...
2,969
Hi Guys, I thought I'd ask a quick question here, a little of topic but if you don't ask you don't get. Firstly we are based in the UK and...
4,078
Just finished a control panel for a Canadian customer. When they received it, they told us it was wrong because all the internal wiring (mostly...
5,295
This should probably be in the classifieds but it is a bit of a rant as well so I am posting here. If you hold a valid IP in Canada and have the...
50
15,028