Can’t change Data ‘Style’

PLCrookiee

Member
Join Date
Jan 2024
Location
Australia
Posts
9
Hi guys have only just been getting stuck into learning about PLC’s. I’ve got an older version of Studio 5000 and a CompactLogix PLC. I have connected a 0-10v transmitter across an input. In the ‘Controller tags’ section I’ve changed the ‘style’ for this input (Local 2:I. Ch1Data) from Binary to Decimal, however when I put in a ‘divide’ instruction and then use that tag it displays as Binary

I have tried right-clicking on the tag and editing the properties but the ‘style’ box at the bottom is grey and I cannot change

Not sure how to go about this one but any info would be much appreciated
 
Copy the value from Local 2:I.Ch1Data to a tag of the same data type but with its style set to what you want it displayed as (its at the bottom of the tag creation dialog). Use that new tag in the divide instruction.
 

Similar Topics

Hi all. I'm trying to set up communication between a 1756-L72 (EN2TR) and a 1756-L82 (CPU port) using produced / consumed tags. From the L72...
Replies
13
Views
372
Hi I have been using Red Lion products for some time, I had a thought over the bank holiday weekend, As you do. It would be nice if whenever a...
Replies
4
Views
1,024
Gents, I've a Beckhoff TwinSAFE project in TwinCAT 3 where I've 2 EL6910 Safety controllers, and need to exchange data between them. So I...
Replies
2
Views
840
Hi, I have to create a log file in Ftview SE when a setpoint is changed on a tag and conirmed with the enter key. Can anybody help please?:lolis:
Replies
4
Views
1,111
Hi, I have to create a log file in Ftview SE when a setpoint is changed on a tag and conirmed with the enter key. Can anybody help please?
Replies
0
Views
630
Back
Top Bottom