Cant change pid values

realolman

Member
Join Date
Mar 2009
Location
here
Posts
584
Compactlogix. Newest version of rslogix 5000. Online editing open up PID dialog cant change values. What am i doing wrong or missing?
Thank you
 
Cross-reference the tag you are trying to change the value of, and look for anything with a "Y" in the "Destructive column of the cross-reference. If there is, then some other code is writing to the tag.

If there isn't a "Y", then the tag could be being written to by a HMI, SCADA, or another controller.
 